factorytalk view me shuttin down

enyew

Member
Join Date
Mar 2016
Location
soest
Posts
2
Hallo,

I have problem in running runntime application in factorytalk view. After loading the application the application shuts down when the run application command is excuted. anybod out there who can help me on this? thanx
 
Hi and Welcome to the Forum!

Have you any Security set up on the Initial Display?

An instant shutdown would typically be seen where the Initial Display has a Security Code assigned to it. The application is always started with the Default user logged in. If the Default user does not have this Security Code assigned to them then the Initial Display cannot load.

You then either remove the Security Code from the Initial Display or assign the Security Code to the Default user.

General practice would be to leave the Initial Display with no Security Code to allow the application to load with the Default user. You can then restrict access from the Initial Display to other Displays as required.

Regards,
George
 

Similar Topics

I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
Replies
3
Views
112
Hello, I'm using FactoryTalk View ME V10. I created a valve as a global object with multiple parameters and when the object is being used at the...
Replies
2
Views
130
Hello all, I was modifying an HMI in factory talk and went to change a go to display button using the ... to select from a list as I had done...
Replies
4
Views
176
Hello, We recently upgraded our control server to a newer model. After the transition we are experiencing issues with our trend graphs to where...
Replies
2
Views
121
Hi, I wanted to ask is there a way to have a visibility expression use the IP address of the HMI (Dynics, not PV) to show certain elements? The...
Replies
3
Views
200
Back
Top Bottom