FactoryTalk View SE - Alarm Ack Log Username
rtgibson
May 2012
Barnsley
44
Hope somebody can help - I've got a real simple View SE (V9) SCADA test application with a couple of alarms setup in the alarm and event server. When I test my alarms they all work etc - question is how on earth do I get it to log who acknowledged the alarm in the details pane. The help file seems to say that it can't be done for alarms and that it only happens for event tracking. Can anybody give me a clue.
Russ
It should be logged by default. The acknowledgement of an alarm is logged as an event, including the station that that performed the acknowledgement, and who was logged in at the time.
Set up a historic alarm & event viewer, and have a look at the entries. You may need to add the respective columns to the viewer to see the data, but whether they're added or not, the data is stored in the database. You can also click on an entry to show more information in the "details" pane (again, as long as you've configured the object to show the details pane).
Hi - thanks for your response, you are correct in that it kind of just works, I think my issue was a dodgy filter on the alarm list. Many thanks for your help. Russ
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
133
Hi all. I´ve got a little problem with my FT View SE alarm window. On my PLC program, I have 200 SINT for alarms, in which every bit is for one...
183
Hello everyone, I am experiencing a strange issue with machine using a PanelView Plus 7 and a CompactLogix 1769 PLC. I am using FTView ME V13...
337
Hi All, I'm currently designing a faceplate for an analog input object, and I'm trying to create an alarm tab with an Alarm and Event Summary...
444
Hello! In FTView SE 13.00 for the AlarmEventSummary1 object I need to add the filter Alarm Name LIKE % %. In the field % % I want to pass a...
547