FactoryTalk View Studio / KEPServer
ASIPLC
Aug 2021
california
I have nuisance alarm that comes and goes. Doesn't seem to stay longer for a few seconds, is there any way I can somehow add a time delay or inhibit the alarm for a few seconds?
What is the mature of the alarm?
Is it a PLC boolean/bit?
Or is it summat else (e.g. an analog value going over or under a limit)?
Welcome to the forum!
The alarm is from a device that's constantly verifying network status, we know it's nuisance, but we also want to know if it is a true alarm after so many seconds/minutes. We use the Wonderware system also and we are able to delay it. This is a a one off customer request, and not sure if we can delay that alarm.
Device -> RedLion DSP -> KEPServer -> FactoryTalk View Studio
No.
It's an analog alarm. If it changes to 1, it will log the alarm.
Thanks!
You say it is analog, not Boolean, but also if it changes to q then it will log the alarm. Is 1 not a Boolean True?
On which of those nodes (device, dsp, keep server, ftv) do you have control of the analog value that is causing the Allen?
I apologize, I'm still a beginner on some of the terminology. It's a pretty long trigger. It looks like KEPServer is creating the analog value.
IF ((({KEPWare.DSP_Woodward.DSLC2G01NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.DSLC2G01ComErr}) || (({KEPWare.DSP_Woodward.DSLC2G02NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.DSLC2G02ComErr}) || (({KEPWare.DSP_Woodward.DSLC2G03NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.DSLC2G03ComErr}) || (({KEPWare.DSP_Woodward.MSLC2T01NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.MSLC2T01ComErr}) || (({KEPWare.DSP_Woodward.MSLC2T02NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.MSLC2T02ComErr}) || (({KEPWare.DSP_Woodward.MSLC2U01NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.MSLC2U01ComErr})) THEN 1 ELSE 0
Simplify & process elimination to find the culprit, something like this to start:
Code:
IF ((({KEPWare.DSP_Woodward.DSLC2G01NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.DSLC2G01ComErr}) || (({KEPWare.DSP_Woodward.DSLC2G02NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.DSLC2G02ComErr}) THEN 1 ELSE 0
You can also add indicators to help troubleshooting, using the above logic but with one pair, like ({KEPWare.DSP_Woodward.DSLC2G01NetA} <> 7544) & NOT {KEPWare.DSP_Woodward.DSLC2G01ComErr})
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
138
Hi all, I'm having an issue with connecting View Studio emulation to a real PLC. I am running View Studio 8.01 on a Hyper-V virtual machine...
262
Hello. I have a Project I'm doing in Factorytalk View Studio. One of my displays I created has a bunch of red x's on all of the objects I created...
699
So, I'm new to the PLC world (fresh graduate) and at my job I've been pretty much only helping out the other programmers with simpler tasks while...
627
Good morning, I have a project coming up that will require my HMI runtime to toggle from English to Spanish via selector switch. What is the...
461