Fanuc 9030 firmware upgrade problem
rainbow_elec
Aug 2008
Edmonton
I am having difficulty trying to upgrade the firmware in a CPU352 and am hoping someone can steer me in the right direction. I have a 352 with firmware revision 8.1 and am trying to upgrade to 9.11, I am connected with an RS232 cable connected to port 2 (RJ11) of the CPU. The connect baud rate is set to "AUTO", odd parity, 1 stop bit. When I try to update the CPU I get a major error message "Target does not support Firmware flash updates".
I downloaded the firmware update just today and am following the instructions to a tee I believe. Has anyone else run into the same problem?
I am trying to test the PLC with Machine Edition 5.8 (demo)but can not upload or download anything to the PLC because the firmware is 8.1. It appears I am communicating with the PLC as I can stop and start the scan but I can't upload the program.
Double check the position of the key switch.
You also need to have the standard GE communication cable. This is the 9pin/15pin RS232-RS485 SNP cable. The notes I have about firmware upgrades for a CPU352 mention the power supply port (15pin), port 1 of the CPU (RJ11) and port 2 of the CPU (15pin).
Good Luck!
Finally
Thanks for the reply. The upgrade worked fine when I used port 2. Port 1 (the one I was trying) won't work for this firmware upgrade.
Hello everyone, We are trying to upgrade a GE FANUC 9030 PLC, but we are having trouble extracting the program from it. LogicMaster90 is able...
1,310
Hello, I Have a GE Fanuc RX3i that I migrated that Has a IC695CHS012 for the Main Rack and 4 IC693CHS392 Expansion Less than 50Ft. I ran across...
1,805
I am converting our Boiler project to a RX3i. Looking at some of the registers for the HMI I see 100r. It is labeled B_1_GPM (Boiler 1 Gallons Per...
2,660
So we currently have a CPU 374+ running a sort of feed bin process. We've had the PLC installed since 2008, with really no problems. I am...
2,382
Good Afternoon I have a few questions regarding Ge Fanuc 9030 series and Modbus. I have a Ge Fanuc 9030 for test Purposes. The Rack Is...
6,978