Fault Logic
jamorenos
Sep 2011
Ohio
Hi there,
I am trying to create a Fault Logic, the scenario is 2 chains that should be running essentially at same speed. I have 2 proximity sensors reading a chain dog on each chain, the dogs have to be sensed at same time to be NO Fault, if they are not sensed at same time this should trigger a Fault and I will use this to stop my system. Obviously conditions that could happen are Chain Dog #1 sensed before Chain Dog #2 and vice-versa. I am using Contrologix PLC V20 with RSLogix 5000, Any ideas ? Thanks for your feedback
It's been my experience that things happening at "the same time" rarely happen at EXACTLY the same time; usually there is some acceptable variation.
That said, I would create two timers; one that looks for the first dog to start it and the second to stop it and the second to look for the opposite (second dog starts, first dog stops). Set your timer presets to the allowable variation time and then, so long as neither timers ever time-out (ie. both dogs are seen within the preset time) all is good. If either timer does time-out, though, you have your alarm.
Could something like this be used to make sure the dogs make the sensors within a certain amount of time. This could be modified to look at the leading edge of the dogs if wanted.
Thanks all for the feedback, the Timer solutions seem to be right, any other suggestion?
@rdrast : could you explain more your concept when you say velocity, how would you do this.
Thanks again
How about just using anti tie down logic.
Thanks Caveman for the reply
I am a little confused, I have used Anti-Tie down when for example you have a semi-automated machine where the operator need to use both hands (so that these are clear from machine) to start the cycle. In my understanding the Anti-Tie down expects to see both input signals to start a cycle, in the chain dog application what if the chain dog #2 comes 1 second after chain dog #1, condition will never be true, am I right?
I don't see how I can use it to check if both chain dogs are sensed at same time to trip the fault.
Would you use an OSR to look for a leading edge? Could you send an example?
Thanks!!
Nice and simple:
Code:
|    Sens_1    Sens_2
|-----| |-------|/|-------+---------(TMR)--|
|    Sens_1    Sens_2     |
|     TMR                           Fault
|    Fault     Reset      |
Dear all , Please I need your urgent help that I am suffering from this connection error fault since days ,i have produced consumed tags with 2...
3,468
Hello guys. CPU showed major fault indication.what could be reason. Kindly help and guide to solve the issue. Kind regards.
1,352
Hey, I'm working on a system that is going to be somewhat modular in nature, and Ethernet based, using CompactLogix and Studio 5000. For all my...
4,496
Good Afternoon, I have a problem that's cropped up in the last few days with a controller faulting on a I/O Connection timeout error 03 16 When...
1,846
Hi guys, I am facing major non recoverable fault in our logic 5573 cpu 1756 L73/A.cpu red LED is blinking. Kindly guide me. Kind regards...
26,932