Charbel Member C Join Date Jan 2012 Location Beirut Posts 307 May 20, 2016 #1 Dear, is it allowed to route fiber optic cable and LV cables in the same conduits? both of the cables are not armored. please let me know if you have any concern. thank you! charbel
Dear, is it allowed to route fiber optic cable and LV cables in the same conduits? both of the cables are not armored. please let me know if you have any concern. thank you! charbel
tragically1969 Member T Join Date Jun 2007 Location uk Posts 1,538 May 20, 2016 #2 Charbel said: Dear, is it allowed to route fiber optic cable and LV cables in the same conduits? both of the cables are not armored. please let me know if you have any concern. thank you! charbel Click to expand... What's your concern ? From an electrical point of view it isn't an issue, nothing is going to effect light flowing down a tube, there may be considerations with cable type and mechanical protection but that's for you to select based on the run.
Charbel said: Dear, is it allowed to route fiber optic cable and LV cables in the same conduits? both of the cables are not armored. please let me know if you have any concern. thank you! charbel Click to expand... What's your concern ? From an electrical point of view it isn't an issue, nothing is going to effect light flowing down a tube, there may be considerations with cable type and mechanical protection but that's for you to select based on the run.
rdrast Lifetime Supporting Member Join Date Apr 2003 Location South Carolina Lowcountry Posts 5,544 May 20, 2016 #3 For the record, we manufacture some medium voltage cables (15 to 300KV) with 6 and 12 strand fiber built in. Can't get much closer together then that.
For the record, we manufacture some medium voltage cables (15 to 300KV) with 6 and 12 strand fiber built in. Can't get much closer together then that.
tragically1969 Member T Join Date Jun 2007 Location uk Posts 1,538 May 20, 2016 #4 rdrast said: For the record, we manufacture some medium voltage cables (15 to 300KV) with 6 and 12 strand fiber built in. Can't get much closer together then that. Click to expand... Interesting, guessing they are used for signals to and from relays for protection etc. ?
rdrast said: For the record, we manufacture some medium voltage cables (15 to 300KV) with 6 and 12 strand fiber built in. Can't get much closer together then that. Click to expand... Interesting, guessing they are used for signals to and from relays for protection etc. ?
rdrast Lifetime Supporting Member Join Date Apr 2003 Location South Carolina Lowcountry Posts 5,544 May 20, 2016 #5 @tragically Yes, and also for the undersea cables, just plain communications.
V0N_hydro Member V Join Date Sep 2010 Location lower mainland Posts 560 May 23, 2016 #6 300 kv is medium voltage ?