First CompactLogix system is it OK?
JeffKiper
Jun 2006
Indiana
2,462
This is my first attempt at a CompactLogix system so please point out any flaws in my plan or any pitfalls to watch out for. The system is going on a plastic extrusion machine so a bunch of single loops are going to be replaced.
System requirements
24 Thermocouple IN
10 Analog Current IN
34 Analog Current OUT
32 AC IN (16 Min)
32 AC OUT (16 Min)
32 DC IN (16 Min)
32 DC OUT (16 Min)
16 Relay OUT (JIC)
I am planning on using AB or Spectrum for the Analog and Thermocouple Inputs.
I have it planned out so the racks are broken up to help isolate the I/O
1 L35E, PA2, IT6, IT6, IT6, IT6, ARM, ARM, ARM, ARM.
2 ARM, ARM, IF8, IF8, PA2, OF8, OF8, OF8, OF8, OF8, ARM, ARM.
3 IA16, IA16, OA16, OA16, OW8I, PA2IQ16, IQ16, OB16P, OB16O, OW8I
I know that I have a lot of expansion room with the ARM card. My boss told me to design for maximum I/O possible so we always have room and do not have to re-label wires when we add on. I am trying to standardize on something anything just as long as it is the same. We only standardize on nothing can be the same.
Going to be out of the shop for the next 2 days so I am not ignoring the help I get from you all. I am just in training.
Guys after I got home last night I thought that about the powersuply loading on the 2 rack. It may be overloaded if I expand the system. If so I will upsize all the PS to the same size.
What you need to do, besides power supply loading is look at both distance from the power supply certain cards can be and connections. The most important would be connections.
There is a configuration book that will allow you to list out your cards and determine the connection requirements to the processor. That will determine if you are okay or not.
David
Hello I am working with a 5069-L320ERMS2 Compact Guard Logix. I am replacing an obsolete Cognex camera with a newer model. Communication is...
1,799
Does anyone know where I can find a table of the CIP Class/Instance/Attribute values for the CompactLogix system settings? Specifically, when...
4,978
Working on a new Compactlogix system. It has a Prosoft profibus card some analog and digital 120vac I/O And a vhsc card. Had everything working on...
2,203
Im wonderring if the is a system variable or its possible in an other way to get information in to the PLC code about the backup battery on the...
3,936
Hi Guys, Do the Compactlogix processors have something similar to the Time Base S:4/14 etc. bits that you get in a Micrologix. I quite often use...
5,656