Flashing output, RS Logix 500
nhicks
Jan 2007
Whitewater, WI
111
Im trying to flash an output (50/50 duty cycle, .5 sec on/off.)
I thought a TON/TOFF setup, but I cant get the logic down right.
Is there an actual timer bit I can use?
NH
How about:
XIC Some_Input XIO FlashTimer.DN TON FlashTimer Pre 100 Base .01
XIC FlashTimer.TT LEQ FlashTimer.ACC 50 OTE BlinkingOutput
Should be that simple.
S:4 bits
If it is not required that the flashing be at exactly every .5 second you could use the S:4 bits to flash the output. Basicly these bits are on then off for a specific amount of time. We use this for our flashing light outputs. Information about and an example of how to use the S:4 bits are located on page B-21 of the SLC 500 instruction set manual (ab cat # 1747-rm001_-en-p[1].pdf)
Larry
Christoff84 said:
I usually use 2 timers for this:
XIO T4:1/DN TON T4:0 0.01 50 0
XIC T4:0/DN TON T4:1 0.01 50 0
XIC T4:1/TT OTE Output
I have to apologize, ive never programmed with this style language.
Can you explain the T4:1/TT OTE command?
The time doesnt have to br .5 seconds, just thought that would be the best, but the flashing needs to be quick enough for the user to glance at it and notice it.
Double click on a line in the ladder diagram.
You will now see the XIC T4:1/DN instructions. It is the nemonic way of expressing the rung. You can press enter on the rung, & enter the rung in using the nemonic commands.
You can also program a flashing out put by using a simple TON timer with time base 0.01, preset 100 and a Limit Test with Low Limit 1 and High Limit 51. Put an XIO instruction in series of timer instruction for recycling it (for example T7:0/DN).
As previously posted, there are several ways to do what you ask, I prefer using the S:4 bits, but the following will work on any platform:
Hello there, Sorry I am quite new to this... thank you for taking the time to answer my thread. I have a small problem trying to get an output...
23
5,109
Hello everyone, I am having issues with an output module connected to my 5069-L306ER PLC. The modules I have connected are a 5069-IA16 in slot 1...
706
When trying to troubleshoot a machine at my factory, I was checking out the PLC and on one of the output cards there were a bunch of flashing...
2,140
Hi everyone, I have an output module that is blinking outputs 6 and 7 even when I take the wires out from the terminals. I thought it was the...
4,930
Hi, I am trying to make an A-B SLC 500 operate a solenoid which in turn operates a cylinder, and would like to get a flashing light when the...
8,347