How are the modules and slots numbered in flex and point I/O?
Is the adaptor where the ethernet or coax cable plugs in slot 0 or slot 1?
What is the max amout of modules per adaptor for these systems?
It looks like point maybe do a lot more modules than flex just me looking at what we have installed around the building.
For the FLEX hardware family, the communications adapter does not have a slot number; the first module next to it will be Slot 0 and so on; the maximum allowed number of modules connected to one adapter is 8 (Slots 0 - 7); if any extender cable is used the slot number will follow the cable path- two horizontal rows containing four modules each and connected via extender cable will be (left to right)"addressed" as 0-1-2-3 (Top) and 7-6-5-4 (Bottom).
For Point I/O hardware, the communications adapter will carry the Slot 0 "address"; I believe you will be able to have up to 63 modules connected to one Point I/O CNet, DNet, Profibus or EtherNet/IP adapter (Slots 1-64)
Thank you very much. Now I understand.
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
149
Hey there, this is my first time trying to use flex io with more than 16 inputs. I am wiring a 1794-IB32 and have looked at the sheet here...
1,318
Hey All, I'm currently building a control system for a large building in a industrial setting. Doing lighting, vent, roof control, door access...
3,506
Hey fellas, Customer had originally requested our services to check the tank levels of 8 tanks then provide a permissive to two Worldwide Drives...
6,416
I have always used flex I/O and have a new install at our plant that they are installing Point I/O. Can someone break down the pros and cons of...
2,177