Hey everyone I have been looking for a wirning diagram for the last hour on the net and haven't found anything yet. Its for a 1794-IB16 module (sinks) Does anyone have any sites that have PDF's on it. Have been to rockwell, and on goolge just can't find a wiring diagram.
Hey lads/Lasses,
sorry to drag up an old thread but im confused on the wiring of the Flex I/O 32 way Input modules. I've had a look through the manuals but I still can't get my head around wiring up the cards.
For each 2 wire input you need to wire one leg to the input channel terminal (0-32) and the other leg down to one of the 8x +V terminals which would mean potentially 4 cores per +v terminal (without using external terminals. the question is:
How do you supply power the module? with other Allen Bradley cards there tends to be seperate terminals for the +V and Com to supply power to the cards with other flex i/o modules there are commons that you link from module to module but the diagram for the 32 way shows these arn't connected.
Thanks in advance,
Lee
Outrage said:
Hey lads/Lasses,
Thanks in advance,
Lee
Last terminal (+V) on the TB (#51 in the TB3 case) feeds the first terminal (+V) of the next TB (#34 in the TB3 case).
You daisy chain through all your TBs this way.
All terminals in between (+V) or (-V) are internally connected to each other.
You need to supply the first and take the next supply oyt of the last one
There's an issue with this type of wiring. The total current cannot exceed 10A. If it does you must wire it in a different way
For 32 point modules you have to split the +V and -V halfway through the TB.
Go on the AB web site and download the following PDF:
1794-sg002_-en-p.pdf
Hope this helps!
Hope this helps!
Bkottaras,
Hi, thanks for your reply, i've checked the document and it does make a lot more sense! thanks for taking the time out to help.
Cheers,
Lee
Hi all, what is the proper way to fuse 1794-IE12 modules? fuse sizes/locations? We are burning up these modules in our facility.
1,731
I have a powerflex 525 that runs on 220 VAC. I wired up power and got into some parameters, but for the most part left it alone. I then got a...
1,973
So i’m Field engineering a panel for a 19’ conveyor we are building. The conveyor will have 3 - powerflex 4 drives. My question is concerning the...
2,429
Could someone show me an example on how to wire the analogic input for lets say channel 0 ?? Ive found this manual...
5,241
Hi guys, I am new to Rockwell Platform and do not understand How to do the wiring of IB32 module. and at terminals 35-51, is Voltage available on...
3,094