Flow rate reading and regulation
Man_Tsi
Oct 2007
Bloemfontein
I have a flow meter which gives out 0.1 litres/pulse,
I'm using a digital input to read the pulse
I'm not sure when to read the pulse i.e. whether every sec,mS etc
so that I can read the flow accurately,so that I can set the alarms for underflow or overflow.
I'm using Cscape to program an XLE osc plc
What I would do is count the amount of pulses every say minute or seconde ,depending on how regular you want your alarms to be updated.then use the amount of counts to determine under or overflow.
As a general rule, digital inputs are too slow for pulse inputs, unless your pulse rate is pretty slow. The plc should look at the pulse every scan, and the scan needs to be at least twice as fast as the pulse rate. So if you are getting a pulse every 20mSec, the Scan rate of the PLC needs to be 10mSec or faster to ensure you don't miss any pulses. Usually a high speed counter module is used to count pulses.
I have many pulse type meters that pulse at 150-200Hz, no way to catch all the pulses on a PLC.
In your case, you may have to reconfigure the meter to output 1.0 liters per pulse to slow down the pulse rate.
Hi,Ken
So generally I cant a use DI to pulse a temp positive pulse bit to count how many pulses I have? And pending on how many litres I need clear the register.
Maybe this will help. The first line is the pulse train with the signal turning on and off at a regular rate. The next two lines represent the PLC's scan with the vertical line representing the instant when the PLC reads the status of the pulse train input.
In the fast scan example you can see that the PLC checks the status of the input much faster than the input changes state, so you could safely count pulse in ladder logic.
In the slow scan example you can see that the first two times the PLC checked the input, it was off. But, in between those two checks, the actual signal turned on and then turned off again. The PLC missed those two events because it didn't check often enough. In a case like this, where the PLC scan is slower than the pulse frequency, you can't count pulses in ladder logic. You need a high speed counter.
____ ____ ____ __
____| |____| |____| |____| Pulse train
_|_|_|_|_|_|_|_|_|_|_|_|_|_|_|_|_|_|_ Fast scan
_|__________|__________|__________|__ Slow scan
You don't have a lot of direct control over the PLC's scan rate. Scan rate increases with the size and complexity of your program and the amount of I/O.
It is more accurate to say that if the maximum pulse rate from the flow meter is significantly slower than the PLC's scan time, you can count the pulses in ladder logic. If not, you will need a high speed counter module capable of keeping up with the flow meter.
As to the determination of what is meant by "significantly slower", having the PLC's scan rate twice as fast as the maximum pulse rate is a good place to start. Remember though, the PLC's scan rate can vary, sometimes over a fairly wide range. Even if the average scan rate is fast enough, there can be occasional longer scan times when an external device communicates with the PLC (for one example). What are the consequences of an occasional missed pulse? If all you need to do is display the rate to an operator, the consequences are minimal. If you are using the pulse train to calculate usage, missed pulses are cumulative.
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
180
One of the engineers has asked me to add code to the PLC to calculate oil flow rate based on delta pressure, using the equation below: Flow rate...
2,821
Hello. I wanted to write the logic of the flow totalizer and the flow itself for self-education in RSLogix5000 V20.01 software. After reading the...
7,658
can any one help with the math for converting an instantaneous value to a totalised value for Gas Consumption usage every hour. in the plant we...
3,249
Hi, I have AB PLC (1769-L30ER) and PV800 HMI in my project. I have a horizontal tank (same dimension) having a height of 200" and capacity of...
2,071