Friday's PID controller design quiz

Another closed loop solution without over shoot.

ftp://ftp.deltacompsys.com/public/NG/Mathcad%20-%20t1p1%20IMC%20Pandiani.pdf

I used the Internal Model Control method to calculate the controller. This is the method use on the www.controlguru.com site. Basicially it is a zero cancelation method.

One doesn't have much control over what the controller will look like. In this case the controller turns out to be a simple PD controller. Notice that the PD controller has a much faster response. Much of this is due to the fact that the derivative gain speeds up the response whereas the integrator gain slows it down.
 
Originally posted by Peter Nachtwey:

Basicially it is a zero cancelation method.

I thought pole/zero cancellation was an iffy proposition since, in practical systems, you can't guarantee that the poles and zeros will stay exactly where you put them. If they move just slightly you will have a significant change in gain over a small change in frequency. Or is this just an issue if the poles and zeros are on the imaginary axis?

Originally posted by Peter Nachtwey:

In this case the controller turns out to be a simple PD controller.

I would have thought a PD controller would be the preferred controller in the first place. Since the process was type 1 it had an integrator already. Granted, in real life you probably need an integrator. But from a purely academic standpoint an integrator in this systems doesn't seem to bring a benefit.

Keith
 
kamenges said:
I thought pole/zero cancellation was an iffy proposition since, in practical systems, you can't guarantee that the poles and zeros will stay exactly where you put them. If they move just slightly you will have a significant change in gain over a small change in frequency. Or is this just an issue if the poles and zeros are on the imaginary axis?
You are right. If the zero drift closer to the origin than the poles the gain will go above 1 in the region inbetweeen. I should add a random number generator to the model after calculating the gains just to see what happens. I have done that on many of my worksheets but for the most part they just confuse the issue...........more. :)

[quote[
I would have thought a PD controller would be the preferred controller in the first place. Since the process was type 1 it had an integrator already. Granted, in real life you probably need an integrator. But from a purely academic standpoint an integrator in this systems doesn't seem to bring a benefit.
[/QUOTE]
Yes, but Pandiani was insistant that the problem be solved exactly as it is. That is why it is academic toruture. In reality I would have a few solutions for the problem. Trying to make one work that can't work is futile. For Pandiani's problem the thing to do is to prove the zero will always be closer to the origin than the pole. Since I have symbolic formulas for these I can find if this is possible. The zero is at -Tp or -1/9*Tm. The pole is at -1/(3*Tm). Therefore the zero will always be closer to the origin than the poles.
 
Last edited:

Similar Topics

Retirement Milestone It’s been an amazing 42 year trip. I have had great fun, seen amazing technologies, met good friends, learned something new...
Replies
36
Views
7,426
I usually can find what answers I need in the archives but thought I'm tired, it's been one of those weeks and I could not find the answer last...
Replies
1
Views
1,929
What is your ‘Strategy’ to these 4 ‘Insights’? This is taken from a slide in a sales presentation done recently, my edits are in ( brackets )...
Replies
1
Views
2,032
For you guys trained by the US Military and Drone aficionados. One of the first Carrier TO&L of a Drone...
Replies
20
Views
5,614
AirAware Credits: http://xkcd.com/1207/
Replies
1
Views
1,726
Back
Top Bottom