I don't get it.
I belive i'm configuring correctly the PLC to power ON/OFF and control the speed set point of the Masterdrive yet I get an error F082 no matter what I do.
Using Simatic Manager I loaded the 315-2DP PLC, added a profibus network, added the Masterdrive communication board, configured PPO 2 protocol.
On the masterdrive I configured the parameters so it starts from the first word of PZD and the setpoint is changed through the second word.
After programming a little bit the PLC, just power up everything.
The PLC sends the start signal to the MasterDrive, it starts, and I can change the setpoint, but only lasts like 5 seconds, then the drive stops showing F082 an the "SF" light of the PLC starts blinking.
Anyone has been through a similar problem?