High Speed Counter on 1769-L24ER-QBFC1B PLC?

alive15

Member
Join Date
Oct 2015
Location
Montgomery, AL
Posts
721
Hello, I want to understand what each terminal does on the Embedded High Speed Counter on the 1769-L24ER-QBFC1B PLC? I read the manual, but I still did not grasp a solid understanding of each terminal block. I want to understand points A0+, A0-, B0+, B0-, Z0+, Z0-, and OUT0. A simple explanation will do, thanks!

A picture of the 1769-L24ER-QBFC1B PLC with the Embedded High Speed Counter is attached.

1769-L24ER-QBFC1B PLC.jpg
 
Basicly a Shaft Encoder will send out 2 different pulse streams. The A pulse is first (if rotated the proper direction) then the B pulse is next 90 deg. out of phase with A.

So if the controller sees the A pulse then the B pulse it knows that the Encoder is rotating in its forward direction. If it sees B then A the controller knows the Encoder is rotating in reverse direction.

The Z signal is not a output in all Encoders. In my industry we will it is normally used for a "Pulse Verification" check. The Z input is normally connected to a Internal switch on the Encoder that will close once per revolution of the Encoder Disk. So if your Encoder is designed to give you 100 Pulses per Revolution. If you use the Z input and if everything is working correct you will see 100 pulses in the HSC Accum register then it will reset and count up to 100 again. By looking at how the Accum counts up to 100 over and over again (repeats) you can say that your Encoder and system is working correctly.

Again that is how we use the Z input but Depending on how you program the HSC it can be used differently. You could use it to reset the HSC at the end of a part run or a manual reset or ??. The manual explains a lot more about how to use the Z input. I am sure there are a lot more people here on the site that could explain how they use the Z input.

Hope this helps.
 

Similar Topics

Hello Folks, Has anyone configured a Momentum high speed counter on Unity 13.1. We need the wiring diagram for Momentum High speed counter and...
Replies
0
Views
82
i am bench testing a 1734 -VHSC24 Point I/O High Speed counter module, i cannot find any examples of wiring the outputs from the module. does...
Replies
4
Views
1,398
Hello guys, I have created a program where I count the high speed inputs of a flowmeter and create pulses per second to check the flowrate. Next I...
Replies
5
Views
1,794
Hello to all, I don't have to much experience in the PLC. I'm using the Studio 5000 v32.03 We are trying to measure the length of a product, in...
Replies
3
Views
1,140
Does anyone know how to set the output window on-off values on the fly without having to inhibit the module? I could of sworn when I first started...
Replies
11
Views
2,386
Back
Top Bottom