How to configure scada for redundancy project in AB SLC 500

siva_maddala

Member
Join Date
Apr 2006
Location
BOMBAY
Posts
63
Hai to everyone

welcome to the automation world. My name is siva. I am working as a PLC,SCADA programmer. Recently i am doing one project by using the allen bradley plc in redundancy configuration. The PLC is SLC 500 . for this i am using RSVIEWME as a scada. Here my query is two racks are there primary and secondary. Whenever the primary got any problem automatiocaly the secondary will take place the action. But regarding Scada how it will changeover to the corresponding primary and secondary.I am attaching the hardware configuration of the project. Please clarrify my query and give the details as soon as possible.

thanks and regards
M.SIVA
 
You're probably going to have to use RSLinx Classic as an OPC server to RSView ME, and use the Alias Topic method to switch between the Primary and Secondary controllers.

More information on the Alias Topics can be found in Rockwell Automation Knowbase Answer ID # 5037.
 

Similar Topics

I have to connect more than 50 no of modbus TCP/IP IO devices to Citect SCADA. I will be connecting them as individual ports. Can I give different...
Replies
0
Views
1,915
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
Replies
3
Views
167
Hello, I am trying to connect a Stride Analog Output module to a 1769 CompactLogix via Ethernet. I added a new Generic Ethernet Module for the...
Replies
4
Views
243
Dear all, I am beginer in ifix hmi programming. I have 2 ifix 6.0 pc with license FiX and client.. Can some one tell me how to configure sample...
Replies
0
Views
157
Hi all, the machine I am programming the Rockwell PLC for has about 100 parameters that need to be adjusted for every customer. I would like to...
Replies
20
Views
1,991
Back
Top Bottom