How to configure the Scalance S615
Greet
Aug 2003
Mol
58
1/ We have a machine with IP-adresses from192.168.0.1 to 192.169.0.30
CPU = Siemens 1511-1PN (192.168.0.1)
Router CPU is on 192.168.0.20
2/ We have a WINCC-station 10.132.127.41 where we want to read data from the 1511-CPU
For this, we installed a S615 to use the NAT-function.
But, unfortunately no succes yet.
We have done this:
Internal adres: vlan1: 192.168.0.20 (router-adres of the PLC)
External adres: vlan2: 10.132.127.33 (range WINCC)
NAT:
source interfave=vlan1
Destination interface=vlan2
Source IP adress=192.168.0.20/24
Use interface IP
Translated source IP adress=10.132.127.33
Destination IP Adress=10.132.127.41/24
Firewall:
Accept From vlan1 to vlan2
Source(Range)=192.168.0.20/24
Destination (Range)=10.132.127.33/24
Service: all
Anyone who sees what we did wrong?
On the wincc-pc we can ping to the 10.132.127.33 but not to the 192.168.0.20
Thanks!
Still not succesfull...
Even if I open totally the firewall (see in attachment).
From my WINCC-station I can ping 10.132.127.33 but not the 192.168.0.20 (or 192.168.0.1).
Normaly it would also be possible to ping these IP's??
Solution:
Destination NAT in stead of Source NAT:
- Destination NAT from VLAN2 to VLAN1
- Source IP 10.132.127.46/32
- Destination IP 10.132.127.33/32
- Translated IP 192.168.0.1/32
Firewall:
Accept from vlan2 to vlan1:
- Destination IP 192.168.0.1/32
I'm having the same problems as it seems you had.
Translated ip was the address from the plc?
Destination ip was an IP assigned into s615 vlan2
Sourcse ip, what was this?
Have you a screenshot of what you set, was this in the NETMAP or Source NAT tab?
Cheers
Ant
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
164
Hello, I am trying to connect a Stride Analog Output module to a 1769 CompactLogix via Ethernet. I added a new Generic Ethernet Module for the...
241
Dear all, I am beginer in ifix hmi programming. I have 2 ifix 6.0 pc with license FiX and client.. Can some one tell me how to configure sample...
155
Hi all, the machine I am programming the Rockwell PLC for has about 100 parameters that need to be adjusted for every customer. I would like to...
20
1,987
Within the last week or so, PME has crashed whenever I try to open a configure IO screen. I am running V8.0 Build 6215. Offline configuration of...
402