hello again. I have been having problems with my control shutting down because of an RTD module fault. When I remove the load from the module it works fine. I have added four additional RTD probe's and I think it has put the power supply over the edge. The power supply I have is a 1746-P4 and it is installed in a 13-slot rack that is fully populated. When I go to I/O configuration and select "power supply" it brings up a message that says something to the effect that the power supply is overloaded. When I remove the four additional RTD's the problem goes away. That being said, how do I select the next larger power supply? Is it safe to assume that the next number higher (P5) supply would suffice? Thank you for the help.
 
Actually, the 1746-P4 is the largest capacity power supply for the SLC-500; it can supply 10 A at 5V and about 2.88 A at 24V DC.

You might just have a configuration that can't be done in a single chassis.

The RSLogix 500 I/O configurator power supply check is a good tool, and there is a nice example of adding up the 5V and 24V loads of various I/O combinations in the 1747-UM011 User Manual and similar summary information in the 1747-SG001 Selection Guide.

It might make sense to split this application up between a 10-slot rack and a separate 4-slot rack for the RTD modules.

Are you using any Analog Output modules (1746-NO4V, -NO4I, -NO8V, -NO8I) ? Most of these have an option to be powered by an external source instead of by the backplane's 24V supply, which might put you back under the 24V limit.
 
When I run only the original four RTD's, no problems. When I run all eight RTD's, the system shuts-down and tells me that the module in slot 11 is generating a generic fault. I then have to shut down the system and restart it. After all 4 channels on the module are checked, I hear something pull-in and then I get a fault on the PLC and it's the slot 11 fault mentioned above.
 
Seems like your P4 power supply is overloaded. See Ken Roach's solutions in Post #3.
 

Similar Topics

Im trying to install a Siemens upgrade license using Automation License Manager v6.0. I clicked D: mistakedly, and now I can not find a way to...
Replies
2
Views
58
Hello, We recently upgraded our control server to a newer model. After the transition we are experiencing issues with our trend graphs to where...
Replies
2
Views
126
Hi all, I really need help with this one. I'm at a complete loss... For months and months, I've had no problems with pressing a NEXT button to...
Replies
14
Views
1,453
Hello everyone, I'm having trouble solving this one and was hoping someone could help. I have a AB CompactLogix L16ER PLC connected to a AB...
Replies
2
Views
592
Is there a way to select a parameter file when loading a given screen based on the value of a variable? I see that under "Global Connections" the...
Replies
2
Views
1,119
Back
Top Bottom