Hyginic master seris FEX Flowmeter

kamau

Member
Join Date
Sep 2006
Location
Thika
Posts
20
Hi all,

I installed a new ABB FEX 300 flowmeter which after a test run for a while it started giving errorneous reading.
It is now indicating a false zero reading(0 L/H) on its display when the pump is running.
What could be the issue?


Kind regards,
D.KAMAU.
 
Since they stopped making the MagMaster, ABB haven't made a new flowmeter that wasn't ****. So that's your first problem...

Is it metal pipe? If not, do you have grounding rings installed?

Is the sensor body bonded to the transmitter with a low resistance earth?

Did you terminate the sensor cabling correctly? If you shortened the factory supplied cable, did you remove the sheath from the screened electrode wires properly?

What is the process liquid?

Is the meter full pipe? No trapped air?

There is a diagnostics menu... does it indicate any faults?
 

Similar Topics

Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
112
Hi i using Kinetik 300 2097 driver control by EIP with using move absolute and incremental for motion , but i want to add same driver and motor as...
Replies
0
Views
64
hello s7-400h and wincc are connected to each other via Ethernet. I need help on how to do time synchronization
Replies
0
Views
65
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
Replies
9
Views
248
I have to start out by saying I am not a PLC programmer and I have basic programming skills but mainly use software as a troubleshooting tool. I...
Replies
0
Views
138
Back
Top Bottom