..another thing. Line 9,11 and 13 can be one line.
Chud, if the Omron ZEN is being used, then there are severe limits on the number of instructions per rung, so probably cannot do this on same rung.
Jaymmzzs,
If you made a list of how this circuit is supposed to operate, then I could do a better job of trouble-shooting. Some possible reasons that you get no output:
1. Check the pre-set value of Timers T6 and T2. If these timers are set to 0 or some small value, then Motor Dumper Output Q0 will not energize.
2. Your Rung 01 contains seal-in logic for Q0, but as soon as T2 times out, it will unseal and stop Q0. T2 is labeled "Latch Motor Timer", but it actually UN-latches motor Q0 after some T2 time period.
3. It appears that your "Start Packer/Dump" I1 Input is supposed to be a momentary-contact pushbutton (as opposed to a maintained-contact selector switch), but some rung logic may not work with momentary-contact logic. For example, Rung 6 will only seal-in AFTER T1 times out. If I1 is only ON for 1/2 second or less, and T1 is set for longer than 1/2 second, then this rung (including Relay R9 and timer T1) will probably never get energized.