I can communicate to the plc but can't ping it
Welcome, well you haven't really provided enough information.
What PLC?
One possibility is there is a router/firewall in the mix that is blocking ICMP ping but allowing the port for AB comms through.
At the end of the day, I wouldn't care. If you have comms, you have comms. Unless you are running SCADA to periodically ping your device for connection status, then program it and move on.
I am trying to use pylogix to read tag values but I always get a None reply according to other forums it's because I can't ping the device, so that is why I am trying to ping.
I can communicate to all of the plcs remotely through rslinx but can't ping to any of them unless I connect directly to the switches inside the cabinets and change my subnet.
/Switch
Check your default gateways and subnet masks if you are traversing subnets.
What does it say when you print the status of the response? Also, what PLC model is it?
Code:
ret = comm.Read("Tag")
print(ret.Status)
Path destination unknown is the PLC telling you the tag doesn't exist. So pylogix is connecting to your PLC. You either have a typo in the tag name, it is program scoped and you are not using the program scope syntax, or its external access is set to None.
Can you post your code?
Pylogix and Micro 820 PLC communication
Nice. You came to the right place, so if you need any pointers, let me/us know.
Hi all,
First of all thanks to dmroeder for sharing links to PYLOGIX for everyone to use. It's a handy tool to have as an automation engineer.
I'm using a Micro 820 PLC and a PanelView 800 HMI on a site to control a small skid. I've set up the HMI to log 3 x Analog values and 1 x Digital value on a USB drive plugged into the PanelView 800 HMI but the records always have some corrupted data in a few rows and logs data normally again.
I've turned to PYLOGIX as a solution and I tried a demo using a Micro820 PLC in our office. I've changed the IP address of the PLC and I've set the Ethernet port slot number of the Micro820, in the Pylogix code, as 2 and added a Digital Tag to start with. However the GUI, of Pylogix, always shows "NOT CONNECTED" on the Left hand bottom of Pylogix's GUI. I can ping the PLC from my computer as always. There're no switches etc. in between. I even tried reading tags by clicking the GET TAGS button on the GUI but it displays "No Tags retrieved".
I tried changing the slot number to 4, for the Micro820, and disabled other network drivers on my computer but no luck yet.
I also tried adding the following lines in Pylogix:
from pylogix import PLC
tags = ['tag']
with PLC () as comm:
comm.IPAddress = 'IPADDRESS'
ret = comm.Read('TAG')
print(ret.Value)
I haven't managed to get it to work yet. Any suggestions would be really helpful. Sorry for the lengthy post.
Thanks..
Code:
tags = ['tag']
    comm.Micro800 = True          ### Add this
    print(ret.Value)
Pylogix connections to Micro8xx need the .Micro800 member assigned a value of True; see the Add this line above, that may fix it.
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
55
Hello i have a PV+1000 firmware ver 5.10 and a compact logix L18ERM VER 24. I googled and read many posts but still can not make simple button on...
561
Have matched communication parameters of both, DOPSOFT HMI and PLC Fatek. Yet an error keeps appearing "Failed to open port COM1". I believe...
688
Dear Members, Currently, I'm working with Hitect HMI spec PWS6600S-S and PLC FATEK PLC FBS-32MAR2-AC. We plan to do a replacement unit...
754
Hi Guys, Here I have Started to work on some difficult task I hope I will get some solution here. I wanted to communicate ABB CI 840 IO Master...
917