I/O Tree configuration

s9k2004

Member
Join Date
Jul 2015
Location
Riyadh
Posts
19
I need help on how to add controller in I/O tree but not listed on module type selection .
The controller is 1756-L71S guardloagix.

Do I need to install any profile to make the catalog appear on the selection list?

See attached selection list..

Thanks..

Screenshot_2024-01-14-23-15-29-48_99c04817c0de5652397fc8b56c3b3817.jpg
 
If the 1756-L71S is not in your local chassis, you need to add the Ethernet Module which you will be connecting through first. Remember, you are not connecting the two controllers directly, they are connecting through Ethernet. So if the remote chassis has a EN2T, you add the EN2T to your tree first, then you add the L71S under the EN2T.
 