IDEC fault memory full
John Morris
Sep 2015
San Antonio
692
Good morning to all you smart cookies
I actually have an IDEC problem I haven't been able to solve. Usually it's AB.
HMI, HG3G/4G-JT22MF, PLC, FC5A-D16RRX1
My predecessor wrote faults into his programming, by that I mean he logged his alarms. Now the memory is full. The Customer has not been able to clear the faults off the screen. I have the HMI programming and the storage method was set to "Fixed".
Does this mean the storage cannot be erased. Does this mean it does not FILO.
Is there an alternate resolution to this predicament.
Your time and attention to this is greatly appreciated.
HAHAH, rare that I get to answer my own questions
Touch and hold the top left corner for five seconds, this brings up the HMI system mode
Open System menu, press "Initial Setting", Press "Initialize", press "Alarm Log" , in that order. this will clear the alarm log data
next time a rookie ( other then my self ) should set "Rotate Data" when setting up an alarm log. FILO.
Damn missed out on a trip to Belgium, too.
Thanks for the space.
Can anyone shed some light, All outputs are high. on FA-2J IDEC IZUMI PLC PLC's RUN light is stable but it's not functioning the way its supposed...
2,131
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
95
I'm trying to establish communication between an HMI DELTA (DOP-B07E515) and a PLC IDEC (FC6A-D16R1CEE) via the RS-232C/485 module (FC6A-SIF-52)...
582
Has anyone interfaced a PLC with a Control Techniques drive Nidec 750 using Modbus TCP? I am attempting to do so using an Automation Direct...
905
I'm involved in upgrading an IDEC FC5A-D12S1E PLC to a FC6A-D32P3CEE. I've attached the original layout of the system. Since then, another HG3G...
448