Idec Plc mobus communications
todell
Feb 2009
CA
18
Thanks to all for the help in the past!!
I am using a Idec PLC model FC5A-D16RS1 with a FC4A-HPC3 Rs-485 module. I want to control the start/stop functions of two Mitsubishi F700 VFD's through Modbus-RTU. I have included the drive manual pages for review. It looks to me that register 40009 is the "control input instruction" the table in the middle is a where bit 1 is the forward command.
This is where I need some help. The Idec support says to use a move command to read and write to registers. What does the ladder look like to set 40009 and start the VFD.
Thanks in advance for the help!!!
I wish I could be of more help, but I don't know much about the Mitsubishi.
I will share this: All the modbus functions can be handled automatically by the IDEC pentra if you simply set them up in the "function area settings".
Your drive must be set up with a matching address. Your function settings in the Pentra will assign the "set coil" function to a code that the drive will recognize as a "run" command, possibly the 40009 you mention. When you turn on the coil in the pentra.... that you have defined in the function area...... the pentra will schedule and execute the modbus function required to "set the coil" in the drive.... if you do the set-up properly, the coil for "run", or "forward".
Sorry I can't help you more.
Stationmaster
Todell, I am not much help on this but I did a job last year using modbus and although it took me a while to grasp what I was trying to do I did find it was relatively easy after that. My biggest thing was I was having to convert OCTAL over at the same time (wont be issue here). That said I did run into something that may be an issue depending on what your are working with... The comms that I was dealing with would not recognize the 40009 so I had to use the 30009? Compatability issue (I think). Seems like starting with 1s and 2s addresses bits and 3s and 4s are for words. I think they are more starting numbers but in case you get to a point where the 4 just wont work try the 3 to see if it is a compatibility thing. Not much help on modbus but I have to say it was not bad after I got it working.
So do I use function 05 to force coil 40009 in the VFD? Or do I use function 06 to preset single register 40009?
In My application I had to use 1.???? to force a bit. Like 1.2113 to force that bit in an Direct Logix PLC. (OCTAL). I could use 2.???? to read the status of an input. I could use 3.????? for a register or 4.?????. Thing is on some of the units (not all were PLCs) the 4s did not work. What I found was I had to use a 3.???? in that case because of a compatability issue. (the vendor of the one of the units told me this) I remeber seeing the 5 and 6 in documentation but it did not apply to my app so I cant help on that. So it looks like 40009 is a 16 bit register. You might have to set bits 0 and 1 or 2 depending on direction as well as give it a speed in 40014 (depending on how it is configured for speed?). 40014 would require a value written to it as opposed to 40009 a bit set. Setting a value in 40009 could get crazy!
So I would write 010000000000000 to register 40009 for forward and 1000000000000000 to 40009 to stop? The speed is controlled by drive PID.
No if you do that you will turn off all the bits in the register except the bit where the 1 is and it is the bit 14 and 15 not 0 and 1. Remember if you write to the register you need to be careful about the other bits in that same register. If you write to the bit it will only effect that bit.
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
112
I'm trying to establish communication between an HMI DELTA (DOP-B07E515) and a PLC IDEC (FC6A-D16R1CEE) via the RS-232C/485 module (FC6A-SIF-52)...
585
I'm involved in upgrading an IDEC FC5A-D12S1E PLC to a FC6A-D32P3CEE. I've attached the original layout of the system. Since then, another HG3G...
449
Hallo all, We are servicing machine automation using PLC Idec FA 2J. I'm trying looking for the PLC user manual, but till now didn't get at all...
795
I have a customer with an Idec FC5A-D12S1E processor. They want to add a few I/O. Yes, this PLC and its output modules are obsolete and thats...
1,058