I dont think the transducer is faulty. I had 3 of them and it is new. All 3 had the same symptoms.
I hook up to oscillopscope and measure the voltage.
at 0psi. it say 16.6v with a 2000 resistance. 1 psi it read 16.8 v. 2psi it read 16.9V. It is so strange. I really dont know what to do to make them align accordingly to linear
 
I dont think the transducer is faulty. I had 3 of them and it is new. All 3 had the same symptoms.
I hook up to oscillopscope and measure the voltage.
at 0psi. it say 16.6v with a 2000 resistance. 1 psi it read 16.8 v. 2psi it read 16.9V. It is so strange. I really dont know what to do to make them align accordingly to linear
Voltage? Who cares about the voltage as long as the mA reading is there.

I think daba nailed this one already. Your transducers are scaled differently than you think they are.

http://www.plctalk.net/qanda/showpost.php?p=441680&postcount=15
 
Put a meter in series with the transducer and verify the above.
I hook up to oscillopscope and measure the voltage.
This is your mistake. Mickey meant for you to measure the CURRENT (milliamperes) in the loop by installing a meter (with milliampere range) in "series" with the other devices already in the signal loop.
 
Hey y'all,

I got an issue with this IF-16 module, why does it only show Channels 0-7 in Offline Mode, I would like to configure Channels 8-15 as I am using the whole card for Inputs

Any input would help out...
 
When you first install the module, you must select Float Data - Single Ended mode. You may also use Integer Data - Single Endled Mode. Either way you need single ended data to see all 16 inputs.
 

Similar Topics

I've got a 4-20ma pressure transducer connected to an analog card on an AB PLC5. Under the setup for the card, I have to set a raw minimum and...
Replies
12
Views
7,386
Hi I'm trying to use a L27erm compact logix controller with high seed input I can see the pulses coming in to a counter but when I look at the...
Replies
1
Views
1,268
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
369
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,145
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
259
Back
Top Bottom