Interfacing Micrologix with S7-300
RTK
Dec 2010
San Diego
18
Have anyone done an data exchange between a Micrologix 1000 and a S7-3xx ?
I guess hardware-wise is possible to use a DF1-to-Ethernet to put the Micrologix in the ethernet... and how's the software-wise, is it possible ?
Are you using Profibus DP for I/O ? The HMS Communicator interface can poll a DF1 device (which the MicroLogix 1000 supports).
http://hms.se/products/products.asp?PID=104&ProductType=Anybus Communicator
There's a Profinet version too, though I'm not totally sure that both support DF1.
http://www.hms.se/products/products.asp?PID=345&ProductType=Anybus Communicator
Modbus RTU is the most common protocol for multivendor integration, but remember that the MicroLogix 1000 doesn't support it. All the other MicroLogix controller models (1100, 1200, 1400, 1500) do.
Hi Guys,
All Anybus Communicators supports both DF1 and Modbus RTU master functionallity. The gateway can also be set up to other protocols, such as Comli or ASCII.
If the Micro Logix PLC allready is set up as Modbus RTU master, HMS has other gateways that can solve it, Modbus RTU slave - to - Profibus slave.
If you have any questions about the gateway, let me know.
BR
Patrick Lansdorf
[email protected]
Ok,
After reading Kens reply more properly, I understand that ML1000 does not support Modbus RTU... So if using the Anybus Communicator, DF1 is the way to go.
Still, let me know if you have any questions..
//Pat
Thanks guys !
Yes, it is Profibus... so I think it will be fine. I use DF1 to Profibus (using the Comunicator from HMS), and then I access the data from the S7 CPU... It will take a while until I get this part... but I'll try to post the results !!
Thanks again !
Thanks guys !
Thanks again !
Hello RTK;
I am sure that the Profibus-DP option will work well.
Another option you could look at is the serial driver for DF1 that can be installed on a CP 341 or a CP 441-2 (serial processors for S7 PLCs).
Part number: 6ES7870-1AE00-0YA0
Description: Allen-Bradley Data Highway DF1 protocol
F,A.Q.: http://support.automation.siemens.com/WW/view/en/1918186
Manual DF1 driver:
http://support.automation.siemens.com/WW/view/en/1218110
Hope this helps,
Daniel Chartier
Hello Experts !! Greetings, Hope you all doing great !! I want to Interface Multiple (Upto 10 ) Barcode Scanner Serially to PLC Micrologix 1400...
2,660
I was wondering if it was possible to take allen bradley micrologix plc's and interface it to ge cimplicity hmi's. If it is possible what do I...
2,040
Hi there, I am developing an application which requires interfacing to a PLC.I will be producing quite a number of the same machine each year. I...
1,571
Afternoon All, I am working on a Project to bring I/O from a MicroLogix 1200(1762-L40AWA) to a SLC 5/05 (1747-L551)NOTE all of this work is...
2,450
hello there, can someone tell me how to interface allen bradley Micrologix 1500 LRP series C PLC with Siemens Protool for runtime data...
4,549