we using a 24 core control cable for motor power and digital input & output.now we start the motor ,found fluctuation in analog output (4-20 ma) which is used for another system. digital/analog input and output is mount same rack. when we separate motor power with a 3 core x 2.5 sqmm. found no any fluctuation in analog output .what is the reason,i want to know. 24 core cable detail is core 1,2,3 for motor power,core no-4,5 for motor brake, core -6,7,8 for torch motor,core 9,10 for slow down limit swich,core 11,12 for end limit switch,core 13,14 for home limit.
please clear my problem
https://www.youtube.com/watch?v=KuUMUvwvML8
Even though your wire is not moving as in the the video, the frequency of the voltage is moving thereby creating a moving magnetic field.
This is even more of a problem with VFD driven motor wiring due to the extremely high magnetic field motion caused by the "carrier frequency".
The solution is to keep your motor wiring well away from your analog signals and shielding the analog signals can help mitigate these unwanted currents.
Hello guys, I need your help. The client has 3 vfds. My colleague noticed that when they ran them simultaneously, the vfds were having analog...
2,355
Hi Team, We have had an old VSD fail (15+ years old) & replaced it with a modern inverter. The brake on this motor is AC as opposed to a DC which...
41
4,118
Good Evening , We had a Mettler Toledo Safeline Metal Detector acting unstable last week . We brought Mettler Toledo in to look at it ...
838
Hi, I have 5 Parker IP66 VFDs, 3pcs 400V and 2pcs 230V. Two of them are located on a filtrating machine and three of them are located on a...
2,006
Hi everyone I have a problem with vfd 3G3-MX2 Omron 1.5KW/2HP/ 3PH. The frecuency driver works fine until another motor start, the other motor is...
2,388