HI TO ALL
I have a maple systems 530t HMI that is connected with a SLC 5/04 processor via a comunication cable. Trouble is the enclosure that the hmi is in collects a lot of moisture. I want to place a heater inside and i'm wordering if this may cause some type of interference between the hmi and the plc, if i run the two cables together, in the same pipe. The heater is a 120 volt 100 watt. The distance between the plc and hmi is aprox. 15 feet. Also I have a 24 vdc running in the same pipe to power the HMI. The comunication cable is shielded.
Thank You.
I have a maple systems 530t HMI that is connected with a SLC 5/04 processor via a comunication cable. Trouble is the enclosure that the hmi is in collects a lot of moisture. I want to place a heater inside and i'm wordering if this may cause some type of interference between the hmi and the plc, if i run the two cables together, in the same pipe. The heater is a 120 volt 100 watt. The distance between the plc and hmi is aprox. 15 feet. Also I have a 24 vdc running in the same pipe to power the HMI. The comunication cable is shielded.