Isolated Analog Output Signal Conditioner - Externally Sourced?
jkelleyus
Oct 2012
Westfield, Indiana
All,
This should be easy but I'm finding it difficult.
I have an older OEM piece of equipment that I need to send a 0-5 vdc analog command signal to... this signal must be sourced from the OEM piece.
Having looked at a bunch of supplier sites it appears all of them source their own 0-10 vdc. Does anyone know of a supplier which allows the output source to be external to the device?
Any help is appreciated.
Thanks,
John
I could see the need if the end device occasionally turns off (or otherwise modifies) its power source thus expecting the input to change. But the commons would have to be connected anyway.
Otherwise, voltage is voltage. With the commons are connected I don't see how it would matter to the end device.
Thanks, everyone. The OEM was the one insisting the vdc had to be sourced from the equipment side. I do see the point that voltage is voltage, but sometimes vendors played tricks with their early control equipment. This piece is a mid 90's induction furnace power supply and the control is based on a Z80 microprocessor board. I'm just trying to be as careful as possible here.....
I'll probably get back to this over the weekend and do some extensive testing with my handy Fluke. At this point I'm not sure why I couldn't just use the 0-10 vdc from my Micrologix 1762-IF2OF2. Tie the commons, send the 0-5 vdc command and go?
Any thoughts?
Thanks again,
John
I'm working with a Siemens S7-1215 PLC for the first time. I typically use isolated analog I/O in my projects, but this particular CPU comes with...
5,074
Hi, Scanner: 1756 - DNB Adapter: 1794 -ADN Module: 1794-IF2XOF2I Problem: The led status in the module 1794-IF2XOF2I is flash green. The bit...
2,373
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
234
I had a question with regards to an Non-Isolated vs Isolated RTD Input Card. This would be for a Flex 1794-IR8 vs Spectrum (1794sc-IF8U or...
1,788
I am stumped. I haven't run into this before. We have a four wire 4-20mA sensor +PWR -PWR +SIG -SIG We have tested it with a process meter and...
17
7,773