ISTACK screen: how to?
phongluu
May 2005
Could someone tell me how to get to the second screen of the ISTACK on the S5 v6.5? It's running on pure DOS, for S5-150U.
I was able to get on the ISTACK but forgot how to go to 2nd page. There was not CONTINUE or NEXT on the page. It must be hidden somewhere.
Thanks all,
P.L
In the manual it only says that there may be several ISTACK screens. It does not say how to access the next screen.
Guesses:
SPACE
TAB
PGDN
SHIFT + PGDN
"+" key
SHIFT + "+" key
ARROWRIGHT
SHIFT + ARROWRIGHT
ARROWDOWN
SHIFT + ARROWDOWN
If you're on the first page of the ISTACK AND yhe PLC is in stop mode, then you can enter the second ISTACK page by simply pressing the INSERT key. Yhe first page is a status page which can be accessed at all times. The second page is the page showing the reason for the interruption of the program, thus can only be viewed if the processor is halted.
Kind regards,
Kind regards,
jvdcande, you are the man!
Thanks,
P.L
I wonder if some one could help me understand the Istack in a 100U. I have a 103CPU which is in stop mode. I disconnected all the expansion except...
2,697
Hi Thank you very much in advance for your help. I am in remote site i would be most grateful if you could help me to know what causes the CPU to...
1,995
Hello! I have a problem with the PLC going in to Stop-mode and the only thing I can find that seems to be wrong is NAUAS (power failure in...
2,588
Now we are facing a problem that our S5-115U is not working proper Last time we have a power failure in our plant and when restart the plant I saw...
4,176
1,972