Without knowing the PLC or the platform the best that can be suggested is a masked AND.
Something like:
AND
I10
00000001
[storage_bit0]
Then when input 10.0 is on that storage bit will be on and you use that bit in your ladder. This way a search may show that the WORD 10 is used, but not 10.1 or 10.0. EDIT: The example is presuming the word is an 8 bit word like Siemen's - if it's 16 bit then add more 0's.
You will have to look in the manual for the programming software you are using to see exactly how it's done for your PLC. The instruction might be AND, MAND, MSK, or a few other labels. Plus determine if the Stop PB is a N.C. contact as it should be for a real world application, or a N.O. contact that the school had if there is a test PLC to run your program in.