I have a plant-wide project pulling data from numerous PLCs (20-30 PLCs) into a redundant Kepware Server. We are talking 2000+ tags. I'm hearing from the Historian development team that are receiving intermittent Bad Quality Tags. When I check in the OPC Quick Client on the Kepware servers, any tags that initially show in a Bad Quality state quickly resolve to Good status. Any suggestions on what I might be able to re-configure in order for the tags to stop failing this way?
 
There is a possibility that when it was configured all tags may be at default scan rate of 100ms, so perhaps if you have some tags that do not need that rate try increasing them, it may help, I have seen systems not RSL though with over 15,000 tags & very few bad quality even at default scan rates but that was on Mitsubishi Ethernet, although connected to the main PLC network the Scada was on a switch next to the PLC's..
 

Similar Topics

OK, this might be simple but I always remembered when accessing rockwell "global tags" or tags at the top level you could just ignore the global...
Replies
2
Views
1,328
Hello dear experts! Please advice me how to generate a digital alarm in FT VIEW SE A&E by one bit from a tag in KepwareOPC where this tag is a...
Replies
1
Views
3,350
I need some help getting the tag info from 1756ebt though 1756dh485/a to a slc500 5/04 channel channel 1. got some info from ab but all their...
Replies
1
Views
1,604
Hi, I am using RSView32 works and Kepware as the OPC. I find it frustrating that whenever i need to add new IO to the scada system, I have to...
Replies
3
Views
3,576
I have a strange Kepware issue I have been dealing with for a few weeks. I have Kepware setup with the Omron NJ Ethernet driver and reading in...
Replies
0
Views
98
Back
Top Bottom