Hi guys!
I have 3 servos for X,Y,Z axis controlled by Kinetix 5500.
In Studio 5000 there is one Predefined tag in AXIS_CIP_DRIVE called "DCBusUpStatus" which we use to determine if the servo lost 400V or not (basically we have alarm for this bit).
I found in rockwell literature that determines DCBusUpStatus bit as: "This bit is set if DC Bus has charged up to an operational voltage level."
Basically we use XIO, if the bit is set to 0 (means DC Bus is not charged up) alarm will be triggered (OTE).
Somehow, I get many alarms in the alarm history that this bit was set to 0, I also wanted to monitor when this happen at what voltage range and it happened when DC Bus voltage was at 550V (which is quite normal operational voltage).
I also tried to put a delay timer for 500ms, but it still manage to pass through.
Afterwards I monitored it more and found out the voltage sometimes drop even to 500V and there is no alarm, DCBusUpStatus is still set ON, so I do not understand why my alarm was triggered at value of 550V.
Afterall since it is OTE, it will always reset itself and continue in operation without any further issue, I am just wondering what could cause this.
Do you have any idea what could cause this issue ?🙏
I will say that I use the DCBusUpStatus to know when it is locked out. If that bit is ever false, my program will stop and prevent all attempts at motion. I feel confident in saying that my servos never see that bit go false except when powered down.
Based on your last comment, it sounds like a bad servo drive.
The DC Bus Voltage is in range min. 543V in rest - max. 785V in movement with all 3 axis, just now I got the alarm at 559V which can't be undervoltage, but I also got CIP_Axis_State 16#0001
Also I've realized, it only happens when axis is not in motion, it stop for awhile and then got straight Pre-charge state
Hi all, I am upgrading a couple of 2094-BC01-M01 servos with 2198-H015-ERS. The original code uses MSG instructions to control (release, engage...
90
Hello everybody, I have Kinetix 5500 (2198-H040-ERS). I'm having issue with this drive. (I believe it's the drive/Kinetix and need confirmation)...
67
Good day: I am wondering if anyone has experience with the Kinetix 5500 S33 Fault. I have 3 drives in a group set as follows: 2198-H025-ERS2...
198
Hi all, New here and new all round to PLC`s. We have a servo drive that runs a cross travel beam backwards and forwards. I am having trouble with...
261