I am trying to configure a simple servo system on a machine that unwinds reels of thin plastic type material. To control the web tension I am writing values to the torque limit bipolar paramter of the axis (there are two on the machine). One axis with a torque limit of zero appears fine wth no torque available at the rotor, the other however always appears to have full torque no matter what value is written to the limit. What else could be overriding the*bipolar torque limit? Any ideas would be most welcome.
RS logix Version?
A bunch of ideas
Are you monitoring /trending "Actual torque"?
There are Positive and negative torque limits that accept settings
You may have to delete the axis then recreate it.
I have experienced a web application that required torque as it was unwinding - ie to maintain the correct web tension the unwind servo had to "motor forward"
This is a previous post, I am realllly struggling to understand why I cannot set the torque limit on two out of a six axis system. I am writing to...
4,107
Want to limit torque on a servo motor (Kinetix 6000 w/ contrologix PLC) so it will stop if there is an obstacle on the travel path. What's the...
4,392
Howdy guys - Looking for some insight on the MAM instruction. Had an interesting one today: I performed a controller upgrade on an older system...
445
Hello everyone: I am looking at the possibility of migrating Kinetix 6000 to Kinetix 5700(460V 3 phase). Reviewing the drive catalog, I have the...
1,156
We have two similar pieces of equipment, one of them uses a Kinetix 6000 for an axis and the other uses a Kinetix 350. When power is removed...
851