Kingfisher to Prosoft issues
CraigM
Jan 2007
AUS
27
I have an installation with a very strange phenomenon.
Hardware is as follows:
ControlLogix rack with Prosoft MVI56 (modbus module)
Kingfisher PC-1 with MC-11 module (RS-232 serial card)
The Prosoft port 1 is connected to the MC-11. The MC-11 is setup as a slave with a Modbus S2 driver. The Prosoft has 5 read commands, reading 5 different blocks of data. Under normal circumstances the data is all valid.
The problem is really random. Occasionally, data being returned for a given command is not from the requested block, it happens to be from a block 110 registers before. ie requested starting address is 41700 but data returned is from address 41590. The offset is consistent but the timing is random. Sometimes once a day, sometimes several times!
We've updated the PC1 firmware (1.43d) and the MC11 is one firmware revision behind (C0156).
If you're wondering, we weren't able to use the PC1 port (DF1) as it is already connected to another PLC not part of our project. Kingfisher themselves are puzzled by this.
Solved
Just in case someone else comes across this sort of application, the solution was to initiate the comms from the Kingfisher MC-11 (set as master).
Would appear the PC-1 couldn't handle being hammered by the Prosoft module.
I am new to Citect SCADA and I am building the graphics for a page that will contain the control of a plant by a Kingfisher RTU. The project I...
278
Does anyone know where I would be able to find the modbus driver for Kingfisher Series 2? (CP-11 CPU). Toolbox32 is asking for a *.d32 file...
1,391
I am currently trying to do the communications between KingFisher PLC CP30 with Citect. Clients are trying to run using KingFish protocol on...
4,469
Hello Forum, Has anyone trialled interfacing the Kingfisher Series 2 to a Allen-Bradley Panel View 300 using the Allen-Bradley DF1 driver? Can...
3,187
Hello I need some manual of hardware and sofware of kingfisher RTU.. Thank´s
2,188