Guys,
Does anyone know of a Millivolt source unit that is pretty accurate for simulating a load cell that is working off of 0-10volt?
Eli
Fluke makes a loop calibrator ( 729 I think, I don't have it right now) and that is our standard. it will do t/c, millivolts, volts, and ma signals.
it's not cheap.
there may be others that use something else.
regards,
james
Do you have a weight indicator? This would be your best bet if you are putting it on a scale. Otherwise you need a solid 0-10V source. I've honestly never heard of "calibrating" a load cell. Usually you do this with weights.
Assemble the scale.
Power up the source.
Mark this as "Zero Weight"
Put on your weight (generally 1/2-3/4 of scale capacity). If it is for commercial use you will have to use certified weights.
Mark this point as your "calibration" point.
Then you have a scale to work off of. Honestly, a cheap weight indicator would save a lot of time/effort depending on what you are doing.
I just realized you want to simulate a load cell. You will want a 0-10V power source and a decade box.
Guys,
Eli
But as I see, the 0-10 volt come through some transmitter. The load cell should be some Wheatstone bridge, and you'll normally need some resistors to simulate it. So if you need to check the loop after the transmitter, you'll need loop calibrator, there are many in the stores (not cheap, as James mentioned).
But if you want to calibrate the weight transmitter, in laboratory , you need resistors, on the machine you'll need known weights, as you have to count a little mechanics in the equation. Normally I give 0 and some known weight near full scale weight, so I can set 0 and span, and after this check with some values between.
Hi. Do anyone know if there are exist any supplier of ready-to-use load-cell and display units, calibrated with certificate and all ? I have...
3,337
hi, How to calibrate load cell of impact plate for measuring flow of solid. we want reading Ton/hr. from load cell our load cell have 0.2004v/v...
3,320
HELLO, I've been a member here for a while but this is the first time i've sasked a question; i usually get the answer or solution i am looking...
20
6,751
Good Afternoon, I’m limited with a skilled maintenance staff to design and build Load Cell , Rollers , etc. for conveyor sections . Do...
666
Good Afternoon , Does Rockwell Automation have an Input Card , maybe in the 1734 series , or CompactLogix series that will receive signals...
862