Looking for Profinet experts on DCP – Discovery and Configuration Protocol

TimWilborne

Lifetime Supporting Member
Join Date
Oct 2005
Location
Roanoke, VA
Posts
2,210
DCP – Discovery and Configuration Protocol packets are well documented, except one field "Xid". This is a 32 bit value, it looks like it has structure 0fxx_yyyy, where xx increments for each new DCP function request, and yyyy increments with each sent packet of the same function.

Any ideas?
 
Tim, hi. I do not have the DCP specification. I work a lot in PROFINET IO development. By looking at a Wireshark trace of the DCP test cases, at least in the case of the RTA (Real-time Automated) tester suite, one can see that the DCP Client (which is the Windows RTA application), whenever it initiates a round of DCP requests, it increments the Xid by one, and all the devices that reply to the DCP request, will echo back the the Xid value that was send by the client. Sorry for not being able to provide more information.
 
Last edited:

Similar Topics

Hi , Where i can find Mitsubishi PLC Card end of line & replacement model details. i am looking for Q02CPU replacement model. Please advice. thanks
Replies
2
Views
126
I have Allen Bradley plcs, I have had Circuit breakers and other automation equipment in the past. There's no solid buyers local. How much do you...
Replies
2
Views
204
can anyone has a good program to learn plc programming online. i have the basic looking into improve my skills thanks
Replies
1
Views
146
I want to monitor a couple signals in a place where there is no PLC but there is ethernet. I know I can use an AENTR or Flex I/O and a module but...
Replies
21
Views
785
I downloaded v24 for studio 5000 but can’t find where the download manager put it! Any help? I’ve done it before but can’t remember. Thanks
Replies
9
Views
391
Back
Top Bottom