M580 input address starts at 1
cm.
May 2018
Earth
Hi All,
We have a curious issue here.
Using Citect SCADA and M580 CPUs, firmware ver > 2.20
When Citect reads %M or %MW addresses, the bits are not offset, i.e. %M40 on SCADA = %M40 on the PLC.
However, for inputs %I or %IW, the address is offset by 1.
i.e. %I40 on SCADA = %I41 on PLC.
We are using MODNET30 for the SCADA driver and just "fixed" the issue by offsetting SCADA variable addresses by 1 - obviously not ideal.
In testing an older M580 with firmware v2.10 with the MODNET30 driver, everything works perfectly.
In the firmware release notes, there is a fix in v2.12 "Fix offset issue when M580 answering to Modbus FC02 and FC04 requests from SCADA". This release is from 2016.
So whatever this "fixed" firmware is doing, there does not seem to be a relevant driver for the new mapping - I have checked all the MODNET protocol differences and none of them match the address protocol of our M580s.
Has anyone come across this issue? If so, what was your solution?
tldr;
M580s return an offset address only when an input is read by Citect SCADA. %M and %MW work correctly.
Thanks in advance.
Hello all, I am wanting to update the system clock via NTP in the M580/M340. I'm aware that we are able to connect to a NTP in the controller...
155
Hi everyone, I'm trying to simulate any program in control expert and see a register in Modscan32 or any software to do that (Like ModbusPoll). I...
107
I'm trying to read modbus data from modbus slave using Read_VAR function. I'm getting an error that my device is not linked to a module. I have a...
159
Looking for some advice on a project. The controller is a BMEP584040. There is a RIO ring with several drops with Quantum I/O. On this ring...
1,026
Our system utilises INPUT_BYTE to capture NMEA0183 ASCII stream which sends data to the NOM multiple times a second. The NOM module can either be...
395