Measuring braking resistor for future sizing.
einnh
Mar 2014
New England
275
I have been working developing winder systems for the past several years. They operate using winders running on AC induction motors and PowerFlex 755's with braking resistors sized for 110% power -- due to what I consider an overhauling layout.
I am not convinced we need braking resistors this large. On every unit I have built the resistors never get much above ambient temperature.
In an effort to optimize the system I wanted to see if there was a good way to measure how much of the braking resistor I am using in order to optimize but due to the nature of how they are used I'm not sure the best way of measuring this.
I know the DC bus is pulsed to the resistor, so I could attempt to measure voltage in those leads but I am not sure if I could capture and log quick enough for a significant amount of time.
Any ideas or suggestions would be greatly appreciated.
Does your system utilize a controlled e-stop? If so, be sure to consider stopping the full load quickly in an e-stop situation before reducing the braking capability.
I asked AB's Tech Connect about monitoring DB usage a year or so ago and this is what they had to say.
"Parameter 935 bit 20 will tell you if the brake is currently on or off
As far as power use testpoint 676
dynamic brake resistor calculated power (i.e. volts * amps for a given interrupt period)
When you put the value 676 in parameter 970 [test point sel 1] the calculated value be put in Parameter 971 and 972 _ "
It worked well for what I needed.
Just an addon thought: Once you have data you want out at the parameter level you can use several methods to record the data. I've used the method above with 3rd party trending software as well as AB's own built in trend tools. I've also tied it to one of the analog outputs of an I/O option board and then set up a volt meter so that I could see what was happening while I was out testing the equipment.
Why not use a line regeneration drive and eliminate the resistor altogether.
It will give you 100% regen 100% of the time and the energy can be used by other equipment.
E-Stops are a little different they require the drive to be in safe mode or disconnect the motor leads either way the motor will coast to stop.
It is except able to have a short time delay to E-Stop the motor at a fast rate using the drive and then when the motor is stopped put the drive in safe mode only a few seconds some safety relays have a built in timer for that purpose.
Hi everyone, I don't know much of PLCs but it happened that i need to connect Leuze AMS358i Ethernet laser measurement to Productivity 1000...
1,063
Hello everyone! Firstly I'd like to say that I'm new to this forum and also new to PLC programming world altogether, that said I really would...
27
4,848
I am looking for a way to determine level in a silo. The material is called Perilite which has a very light density. Bulk density could be...
2,750
In our water cooling tank, I've installed and successfully wired up 4 float switches & updated the PLC (big thanks to @parky for that). As a...
46
11,472
Hello, I have an application where I need to measure the salt level/volume in a salt saturator. This is a fairly large tank where we load bulk...
21
6,510