Micrologix 1100 fault code
Hannic
Oct 2015
Viborg
Hello.
I have recently got a micrologix 1100 from allen bradley for my home projekts. I have tried to download a program to it but when i had downloaded the program it came with a fault code.
Fault code: 0489h Major error.
What does the error mean??
After the code came, the plc lost its ip address.
Hope someone can help me :)
See pdf. Take note of notes 1&2. Especially module 4.
Check to make sure the I/O modules are plugged in properly.
You might try removing the modules and try downloading a simple program without expansion modules to make sure the processor is ok.
Hmm, only two posts. Will they come back?
While we wait...
If a user gets this error code on a MicroLogix, then you are advised to go to Function Files, IOS tab and look for the offending module and take note of its extended error code. This can then be looked up in the literature for the module or on the Knowledgebase...
46699 - Error code xx89h on a MicroLogix controller
Access Level: TechConnect
Regards,
George
The solution was that i had made a wrong module setup. Gave the PLC a new IP so i could find it, and then made a new program with the changed I/O modules. And downloaded it to the plc and the fault was gone. :)
While I'm tipping...
These kind of configuration errors are a good reason to use "Read IO Config" under the I/O Configuration when you have a valid path to the controller. It will automatically populate the correct I/O Modules for you...
522820 - Read I/O Configuration button in RSLogix 500
Note: This is done while offline.
Regards,
George
On a Micrologix 1100, a card failed. After replacing the card, there is a fault 0187H. What does this fault mean and is there a way to clear the...
1,473
Dear All, I've a problem with MicroLogix 1100 fault LED solid. I'm trying to upload file from this device. But I can't to go online with Rs-232...
2,713
Please I have a Micrologix 1000 that keeps blinking a red fault light each time the machine is put on. What should I do to clear this fault?
4,036
ML 1100 is going to fault with code 0020h.What will be the reason.How we can solve it.
7,312
my micrologix 1100 just went into a blinking fault state when i tried uploading a different program with a different ip address. the fault code is...
19,882