Micrologix 1200 - 'Other card detected - No current load'
ENA-nbruins
Jan 2020
Hamilton ON
Hello
I am currently having an issue with setting up a AB Micrologix 1200 system with a 1762-OB32T output card.
When setting up the card in the I/O Configuration it sees the card as 'Other' with the description being 'I/O Module - ID Code = 100'.
I tried uploading the program to the controller and it gives me this error
"WARNING: 'Other' card detected - no current load was taken into account for the card(s)"
I did see there was a similar post made in 2010, but no solution was given. I also see that there is some info on the rockwell knowledgebase but its behind their paywall.
Has anyone figured it out? Is there anything I can do?
Cheers
It's probably the current FRN (Firmware Revision Number) running on the CPU. 32 Point I/O modules are relatively 'new'.
Unless exceeding the ML1200 maximum allowed I/O point number (136) you should be able to freely download the latest available ML1200 FRN (14.000) and ControlFlash the controller into it thus allowing the addition of a 32 Point DO expansion module.
Thank you both for your reply!
First, I tried updating the firmware to version 14, but I ran into a bunch of errors that prevented me from updating, reverted back to firmware version 12
As far as setting up the "Other" I/O module goes, I think we are good.
The Advanced Config for the card looks the same as what posted on the KB post. The only difference is that I have a revision box. It's currently set to rev A.
Unfortunately its still not working, still getting the same errors o_O
i am trying to add an expansion card to a micrologix 1100. i am only testing as the real addition will be on a 1200. currently im unable to add...
2,045
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
689
I have a MicroLogix 1200 that has an 8 input and a 16 output. Every 6 months-year I get a fault and when online go to error it is something like...
518
Have a bad output on a Micrologix 1200. Moved wire over to an available output, changed program to associate with new output. downloaded program...
763
I need help achieving the following task: ML1200 sending 4 to 20 mA thru analog output ch0 to a DC speed controller analog input(4 to 20 mA) my...
679