micrologix 1400 PID
Jan 2013
california
32
First time using a PID instruction on a micrologix 1400 Platform, my issue is putting the PID instruction in manual and writing to the CV for manual operation of the loop. I set the AM bit true and should be able to use a MOV instruction to write my manual percentage to address PD#.CVP correct? From 0 to 100? I tried this and I cannot control the control variable manually, I have to set the AM bit true and write directly to the output. Also when I switch the PID instruction from manual to auto, my PID output isn't exactly smooth, is there a way to perform a bump less transition from auto to manual. This PID is for a heating temperature control loop.
You write to the "CV" (PD??.?.CV) when in the manual mode to control the output.
See PDFs below.
Instruction set if you need it. Chapter 20.
http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1766-rm001_-en-p.pdf
To get a bumpless transfer going from manual back to auto you need to write "MOV" the PV's value to the Setpoint while in the manual mode. You may have to readjust the set point after going back the the auto mode. The actual values 0-16383 or engineering units will depend on how you set-up the "Set-Point Scaling" see manual for more info on this.
HI - I have a tough process and have been struggling with controlling my PV using a Micrologix 1400. I uploaded the file, changed .rss to .txt...
2,004
I have 2 no.s Micrologix PLCs used for PID control variable output to 7 no.s VFD drives.2 no.s are used as i have no spare analog cards for analog...
1,531
in micrologix 1400 we have to enter duty cycle to get particular duty cycle.But i want my duty cycle changes according to values coming from pid...
2,627
I am having trouble with PID instruction. I have done this many times with a SLC500 but not with the Micrologix 1400. Basically I am confused on...
3,151
I've got a control loop that I can't quite figure out how to accomplish. Three variable speed wells feed water to a tank, the tank supplies water...
4,014