PID Micrologix 1400
Wendon65
Oct 2015
Connecticut
I am having trouble with PID instruction. I have done this many times with a SLC500 but not with the Micrologix 1400.
Basically I am confused on the setup for the PID.
PID File(I am using the PD9:0
I am using a 1726 IF2OF2 I/O card for my 4-20ma Input I:1.0 Xducer
and 4-20ma output O:1.0 to control a VFD
I am using a touch panel to choose a setpoint (SP)
I am getting an instruction fault when downloaded to the ML1400
Thank you for any help on this
Welcome to the Forum !
What exactly is the text of the error message ?
Is it a message generated by RSLogix 500 during compiling and download, or a fault code that appears when the controller is put into RUN mode, or something else ?
Hi Ken, In the data status file window I have an error of an Invalid PID instruction parameter. I am still messing around with it, but cannot seem to identify what that might be
The more information you can provide, the better.
The whole *.RSS file would be ideal, or a screenshot of the PID instruction setup might help too.
Just got off the phone with tech support.
I had 1 parameter in the PID setup screen that was not changed. There is a note in the manual that describes this. Factory default on the loop update tuning parameter is 0.0. This must have a value. changed it to .1 and the program can now go into RUN.
Thank you for your help. I hope this post helps someone in the future
HI - I have a tough process and have been struggling with controlling my PV using a Micrologix 1400. I uploaded the file, changed .rss to .txt...
2,004
I have 2 no.s Micrologix PLCs used for PID control variable output to 7 no.s VFD drives.2 no.s are used as i have no spare analog cards for analog...
1,531
in micrologix 1400 we have to enter duty cycle to get particular duty cycle.But i want my duty cycle changes according to values coming from pid...
2,627
I've got a control loop that I can't quite figure out how to accomplish. Three variable speed wells feed water to a tank, the tank supplies water...
4,014
First time using a PID instruction on a micrologix 1400 Platform, my issue is putting the PID instruction in manual and writing to the CV for...
4,454