micrologix 1500 forced bit in Rsview32

hasabeanil

Member
Join Date
Mar 2004
Posts
13
Hello to everybody,
I want to show the forced bit of Rslogix 500 in RSview32. I am using Micrologix 1500 28BXB.Is it possible
Thanx
 
Hello to everybody,
I want to show the forced bit of Rslogix 500 in RSview32. I am using Micrologix 1500 28BXB.Is it possible
Thanx

I ran this by Rockwell Tech Support, and at first they indicated it was possibe. When I asked them for specific details on how to make it work, they then said it wasn't possible. They have since withdrawn the Knowledgebase Article that indicated it was possible.

I found you can monitor the Forces Enabled S:1/5 and Forces Installed S:1/6.

Stu......
 