Micrologix 1500 OF-2

olias

Member
Join Date
Apr 2002
Location
North Jersey
Posts
185
Easy one for you guys.This is my first time with analog.
How do I configure the output module for 4-20ma. And then, how do I convert RPMs to 4-20ma? "Help" doesn't.

Thanks in advance.
 
Click on the IO Configuration in the project listing on the left side of the RSLogix screen, highlight the output card, and then click on advanced. From there on it is fairly straightforward to configure the card.

To convert the rpm data to the card 4-20 mA output use the SCP function.
 
Thanks. Set up the card, but didn't understand how the card would know what I wanted. Didn't know about the SCP function.

Olias
 