Micrologix 1500 won't connect - did it die?
zephxiiii
Aug 2018
Fort Wayne, IN
So I have a Micrologix 1500 LSP that was running a test station, but suddenly stopped (while I was on vacation).
It lights up with the power light, run light lights up when switch is put into run mode, and the COMM 0 light blinks here and there. If I push the DCOMM button, DCOMM lights up... but I can't connect to it from laptop using the front port.
Now if i plug my cable into another one that is running, it shows up in RSLinx as available etc., but this one will not.
I'm pretty much a newb so looking for some suggestions.
Just a guess... but pushing the DCOMM button will switch the COMM's but if you push it twice it will switch back, how many times did you push it
Also try clicking auto configure again in RSLinx configure (assuming you are using the DF1 driver)
After you push the DCOMM button. You are using DF1 protocol? And what happens when you click on autoconfigure?
You might also try configuring RSLinx manually to the controllers default setting, see pdf.
Edit: geniusintraining types faster then I do.
Putting it into DCOMM mode, auto configure driver, then closing and restarting RSLinx got me back into it.
I forgot to see if there was a program inside it though which sucks. I just downloaded the one that was in it again and it started running again. I even pulled the power to it to see if it would restart and it did.
Not sure why it stopped running like that, had been going for a couple of years at least no problems. All it is, are some timers that cycle a couple of outputs.
I'm working with a Micrologix 1500 (1764-28BXB)on a machine and I was trying to get it to talk to a panelview 300 micro (2711-M3A19L1) directly...
4,240
91
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
107
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
922
Hello folks, Hope everyone is doing fine. I got an OMRON NS10-TVOOB-V2 hmi screen last day and planning to use it with Micrologix 1500. 1. Is...
1,211