I am trying to connect to a AB micrologix 1500 controller but have failed. The communication settings I have tried are as follows:device: SLC-CHO/MICRO/PANELVIEW, BAUDRATE: 19200,PARITY:NONE, STOP BITS:1,STATION NUMBER:00,ERROR CHECK :CRC, PROTOCOL:FULL DUPLEX, DEVICE NAME :AB_DF1-1
I have tried the switch settings on run, rem,prog and still fail.I need to connect and alter the conveyor prog. I have worked on the micrologix 1200 before but didnt have problems.
What am I doing wrong?
Mat.
Is there anything else connected to the Channel? If yes then check the communications setup this device uses.
If there is not then look at the Channel LED in order to determine the correct communication protocol.
If it is OFF then it is likely to be set to DF1 protocol. When connected to another DF1 device the LED will flicker rapidly with channel data.
If it is pulsing slowly green then it is set to DH485 protocol. The slow pulse is the port looking for another node to connect to. When it finds one it will go solid green.
Once we know what comms you are using we can progress to the correct settings, or troubleshooting the serial port on you PC.
A Proface HMI is connected on the 9-pin D connection and comm1 is flicking fast.There is an 8-pin connection which I am trying to use , where I am plugging the 1762-cbl-pmo2 c series cable.
There is a "COMMS" button behind the big plastic cover on the front of the Micro 1500 that is right in the center towards the top of the unit. I would push that button until the DCOMM LED turns on and then let RS Linx autoconfigure it's setting to the PLC.
You can then go online with the PLC and verify the actual port settings.
129
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
125
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
941
Hello folks, Hope everyone is doing fine. I got an OMRON NS10-TVOOB-V2 hmi screen last day and planning to use it with Micrologix 1500. 1. Is...
1,220
Good morning to all, I need to modify an existing PLC MIcrologix 1500 configured with a Modem on Channel 1 (DF1 Full Duplex) and an...
1,443