I am experiencing an issue with the profibus modules on micromaster 420 drives. I would bet others are having the same problem so hopefully someone has a good solution or we can develop one together.
We have been getting intermittent F0070 faults on the drives for some time and after trying several things to eliminate the issue believe that we have identified the root cause. We noticed that we were able to create and eliminate the fault condition by applying a couple pounds of force, in tension and compression respectively, to the communication module mounted on the front of the inverter. Pulling on the module would cause the profibus status LED to turn red indicating a loss of communication with the inverter. Pushing on the module would reestablish the connection, this also worked to reestablish drives that randomly faulted on their own.
Upon investigation it appears the clip that retains profibus module to the inverter is not sufficient to maintain the electrical connection between the two devices. The plastic case shows no signs of excessive wear or cracking. This seems to be a design flaw in the plastic enclosures.
I have put some thought into possible solutions but am trying to avoid several things: I would prefer not to modifying the enclosures (i.e. cutting the plastic). I need to be able to easily remove the operator interface (BOP) that attaches to the front of the profibus module.
So my question:
Is anyone else experiencing this issue?
Also, has anyone developed a solution?
We have been getting intermittent F0070 faults on the drives for some time and after trying several things to eliminate the issue believe that we have identified the root cause. We noticed that we were able to create and eliminate the fault condition by applying a couple pounds of force, in tension and compression respectively, to the communication module mounted on the front of the inverter. Pulling on the module would cause the profibus status LED to turn red indicating a loss of communication with the inverter. Pushing on the module would reestablish the connection, this also worked to reestablish drives that randomly faulted on their own.
Upon investigation it appears the clip that retains profibus module to the inverter is not sufficient to maintain the electrical connection between the two devices. The plastic case shows no signs of excessive wear or cracking. This seems to be a design flaw in the plastic enclosures.
I have put some thought into possible solutions but am trying to avoid several things: I would prefer not to modifying the enclosures (i.e. cutting the plastic). I need to be able to easily remove the operator interface (BOP) that attaches to the front of the profibus module.
So my question:
Is anyone else experiencing this issue?
Also, has anyone developed a solution?