Hi,
My MM430 keeps issuing fault F002 everytime it rampdown to stop. The load is only a centrifugal water pump. The ramp time is 3 seconds. Need your help. thanks
 
Overvoltage

Dear junmontes,

You get F0002=Overvoltage because when you are stoping the pump, the motor works as a generator, but the DC cicuit inside the MICROMASTER can't give energy back to the AC network (because the input is a rectifier). So you can:
-Increase stoping time.
-Put stoping time = 0 so It wil coast down.
-Set P1240=1 That extends breaking ramp to prevent F0002.

Note: In MM430 doesn't have choper for controlling breaking resistor

Sincerely,
Kelkoon
 
JesperMP said:
Or set it to coast to stop.
Why use ramp down with a water pump ?
Is it critical to cut the pressure fast ? If so, use a quick ramp down + brake resistor.

When you are using a bermad valve, or you dont have a non return valve you have to use a ramp down until the valve is fully closed then only can the motor come to a stop.
When using free wheel stop you get water hammer when stopping....not desirable
 
just increase the ramp down time......gradually. If you increase it to long it will also trip. What size motor is it?
 
Hi! Guys,
Thanks for your valued replies.

chudjust increase the ramp down time......gradually. If you increase it to long it will also trip. What size motor is it?


JesperMPThen your options are to increase the ramp down time, or add a chopper + brake resistor, or exchange the MM430 with an MM440 + brake resistor.
KelkoonDear junmontes,

You get F0002=Overvoltage because when you are stoping the pump, the motor works as a generator, but the DC cicuit inside the MICROMASTER can't give energy back to the AC network (because the input is a rectifier). So you can:
-Increase stoping time.
-Put stoping time = 0 so It wil coast down.
-Set P1240=1 That extends breaking ramp to prevent F0002.

Note: In MM430 doesn't have choper for controlling breaking resistor

Sincerely,
KelkoonYesterday 10:33 AMJesperMPOr set it to coast to stop.
Why use ramp down with a water pump ?
Is it critical to cut the pressure fast ? If so, use a quick ramp down + brake resistor.Yesterday 02:21 AMMarshyHi,
Try increasing the deceleration time. Also do you have a brake resistor fitted?

The drive has no brake resistor. The motor is 30kw. I will consider the braking resistor but for the meantime I'll try to play with decel. time and the mode of stopping the motor. Keep you posted. Thanks
 
If you are pump up into a line (normally) dont use coast stopping. Like I said you will get water hammer
 

Similar Topics

It is first time we are working with CANOpen. There is a task to control Siemens Micromaster430 from Modicon M340. We've got EDS from Siemens...
Replies
5
Views
5,187
Hi Can i plug an AOP into a siemens 430 MM invertor ? The AOP is listed for the 440 only, the 430 uses the BOP2 ? Reason i ask is i just had a...
Replies
1
Views
6,111
Does anyone know where to get spare parts for Micromaster 430 37kW. It seams that my burn out while moving to new electrical cabinet. It’s BOP was...
Replies
5
Views
4,775
Anyone have any experience with these critters? Looking to control process water pressure in injection molding operation.
Replies
2
Views
5,670
Hello Everybody, Recently we changed the gearbox which has different ratio than the original one on a motor which is controlled by Micromaster...
Replies
3
Views
1,902
Back
Top Bottom