Mitsubishi FX2N repair -- schematic for PS
johng23
Aug 2011
Ennis, Texas
I have a FX2N-48MR that has a failed power supply board (FX2N-48/80). Is there any legal source for a circuit schematic for this board? The power supply board also bears the following text: JY331B85901E.
Have you tried to get an external power supply and wire the positive to your inputs and wire the common of each together? I had this same problem with an almost new mitsubishi plc and this solved my problem.
No, not yet. I am guessing that the power supply board produces both 5V for the processor, and 24V for the digital inputs. What voltage should the suggested "external power supply" be?
I believe the board just reduces the 24VDC to the 5VDC for the processor and then just switches the 24VDC through your outputs. It's an easy fix and much cheaper than replacing the PLC. I would use a 24VDC power supply.
Just a thought, but I've had a FX1N power supply go down in the past and it's been a small surface mount fuse on the PS board that was the problem. May be worth a check, this tends to happen when an external power supply is connected to the on board 24v by mistake!
I suspect he will have checked the fuse - as he has the board part number.
However here's a neat trick I'd like to bet none of you have seen before.
When I first came across it in a panel, I remember thinking 'what the .....'
Take the live and neutral completely away from the plc and put your 24V dc supply unit straight on to the 24v and 0v terminals.
The plc works fine negating the onboard (blown) power supply.
After I knew this, I once had a old FXon with a dry joint somewhere on the power side. It would run ok then all the lights would go off. A tap or squeeze of the plc would bring it back to life. I connected a 24V dc supply as described above (removing the 240V ac) and it has worked flawlessly for many years now)
Thanks Goody,
We had a prox switch short out and blow the 24V, so the PLC looked like it was a gonner.
We disconnected, the L1 Hot, and L2, and connected 24V DC to the bottom, and wallah! it came back to life.
I know, we could have taken apart, and de-soldered the fuse, but this gets us back up and running so much quicker.
I've worked on one Mitsubishi PLC in the past 40 years. Now, it looks like I get to tackle another one...using GX-WORKS3-C1 software which I...
964
I have been asked to work on a Mitsubishi Melsec FX2N-80MR PLC but have no experience with Mitsubishi at all. The hope is to get online to find...
1,350
Hi all IÂ’ve never worked with Mitsubishi PLCÂ’s or software, but a customer at our branch has requested the PLC program for future...
787
1,646
Dear all, I have a FX2N-20MR chinese semi-clon of a Mitsubishi PLC. It has only a serial DB9 port that cannot be removed or exchanged (which is...
2,109