TWControls said:
What is the part number of the Panelview? Depending on it's communications protocol it may be able to connect

As TW said, can the Mitsubishi do modbus. You need the right PV

ModbusPV600.jpg
 
Last edited:
Long time since i did a PV, i forgot about Modbus etc!

I dont think the FX2N has any modbus capabilities but you can get a Profibus FX2N-64DP-M Master adapter for it.
 
Also it should work fine with Devicenet and there is a slight possibility of it working with Ethernet but would have to dig a little deeper to find out. Need a part number before I do that much digging
 
Thanks everyone for your valueble comments. I think I can connect PV600 to FX2N by RS232 comms. But in Panelview, How can I refer tags to MITSUBISHI addresses(eg. X, Y, D, M Etc).
 
I don't believe your MITSUBISHI supports DF1 protocol. But I have never used one. If it doesn't then they are not going to talk.
 
It would need to end in a 14 to support modbus. You may be able to find an intermediate converter for your application
 

Similar Topics

I've worked on one Mitsubishi PLC in the past 40 years. Now, it looks like I get to tackle another one...using GX-WORKS3-C1 software which I...
Replies
3
Views
952
I have been asked to work on a Mitsubishi Melsec FX2N-80MR PLC but have no experience with Mitsubishi at all. The hope is to get online to find...
Replies
4
Views
1,340
Hi all IÂ’ve never worked with Mitsubishi PLCÂ’s or software, but a customer at our branch has requested the PLC program for future...
Replies
0
Views
784
Hi all IÂ’ve never worked with Mitsubishi PLCÂ’s or software, but a customer at our branch has requested the PLC program for future...
Replies
8
Views
1,637
Dear all, I have a FX2N-20MR chinese semi-clon of a Mitsubishi PLC. It has only a serial DB9 port that cannot be removed or exchanged (which is...
Replies
5
Views
2,083
Back
Top Bottom